Plumbing System Drawing Development

Discussion in 'AutoCAD' started by Dave Alexander, Apr 16, 2004.

  1. Not sure where this is going to go but......

    I have always done plumbing systems in a single drawing working vertically
    through the building using layer names with a level. ie. 1NPSAN is first
    level new plumbing sanitary drainage while 2NPSAN is level second level new
    plumbing sanitary drainage. All you do is configure some menu macros to
    switch the layers from level to level as well as current layer from level to
    level.

    I can't do this anymore because the company is very large with 13 different
    branch offices and one cad standard system which doesn't support the use of
    layer names with levels. When I ask how do they do plumbing, they say that
    they just have all the separate building level plumbing drawings open and
    simply "copy with base point", riser locations from one level to the other.

    When I suggest one drawing with all levels in the one drawing, the first
    thing they tell me is that they cannot have only one person working on all
    the plumbing drawings at one time as they have to be worked on by more than
    one person when it comes down to the "crunch".

    I have broached question of changing the layer names to support multi-level
    plumbing drawings but have run up against the company "cad standard system"
    which it appears to be "impossible to change". That is another issue and I
    don't want to get into that.

    So back to my question. I have tried to work with the "copy with base
    point" - "paste" method with some sucess but find it slow and tedious. I
    have also been told by people from other companies that they xref in the
    other level plumbing drawings for reference and if no one else is working on
    the xref dwgs, they use "refedit" to change the other level dwg. This also I
    have tried but find that the problem is in keeping the same relative view
    when working in one area. The next thing I tried was creating a drawing with
    all the architectural floor plans attached and remaning the xref to 1-arch,
    2-arch, etc and then attaching a copy of the plumbing from each level
    plumbing drawing.

    Now having just said that, I realize that I should have simply attached each
    level plumbing drawing, renamed the xref and frozen out the architectural or
    better yet made the xrefs in the level plumbing drawing "overlay" instead of
    attach so that all I would get is the plumbing itself. Now, I can manage the
    layers by typing -layer off N (leave current layer current) ON 1* to get all
    level one layers to display. Then layer on again to turn on the 2-P* level
    plumbing on for reference. This is not half bad.

    What I would like from others is any hints, comments or tips in working with
    individual level plumbing drawings.
    If you want to work the other way with all the floor levels in one drawing,
    I can help you with that.

    Dave Alexander
    Keen Engineering Co. Ltd.
    www.keen.ca
     
    Dave Alexander, Apr 16, 2004
    #1
  2. Dave Alexander

    slacker Guest

    Dave,
    Have dealt with exactly that same issue for years. Basically, all
    facility systems (elec, mech, hvac, I&C, plumbing, etc) had a separate dwg
    file for each level, so that more than one person at a time could work on
    pieces of the system, across multiple offices in different states (and/or
    countries depending on the project).
    Each system dwg of a specific type had a similar name, with the
    appropriate level # appended at the end (plumb-1.dwg, plumb-2.dwg, etc.).
    Layer names were not set up by level, they were the same on all levels. If
    you had a need to show more than one level at a time, you used xrefs, and
    used some smart filtering to toggle displays as needed.
    They had a strict policy of absolutely no refediting, set up all the
    dwgs to disable it, and also used custom document management software to
    check in/out the dwgs, so if you somehow still managed to refedit an xref
    that someone had checked out, your changes would be overwritten when the dwg
    was checked back in.
    They also dictated up front where the cutoff was for each level - top of
    finish floor, bottom of slab, whatever. That was then the cutoff for what
    when in each level's dwg, components/assemblies did not matter, it was
    specifically dictated by where it would be located in space even though
    there was no 3D. If a one-piece fitting - such as sweep elbow - went through
    the cut off point, it would go on whichever level the majority of that
    fitting would physically be on, and if it was really close enough to be
    even, then it was up to the designer.
    Once you got used to it, it actually wasn't so bad. Granted, it takes
    some good documented standards, and conscientious use of them, especially in
    the use of layer names & properties in each system. Spelling errors were
    always trouble - "pipeing" vs "piping", stupid stuff like that. Those
    sometimes elude easy filtering. They did have some decent menus and
    customization in place to help everyone stay as standard as possible, and
    most people recognized the value of trying to make sure that things were
    standard from dwg to dwg. (I did say MOST people.)
    But here is where it got sort of ugly.
    All the system models had xrefs (only as overlays) for reference in
    drawing the system. Sounded good, but what ended up happening was that
    basically every system dwg had every dwg of all the other systems overlaid
    into it, which was then loaded/unloaded as needed by whoever was working in
    the dwg at the time. Seriously, some of these dwgs would have more than 50
    overlaid xrefs in them. But then every once in a while a single dwg would
    get screwed up (a lot of times by the infamous null block "" from R14 to
    R2000 conversion), which would then cause every dwg that had it referenced
    to crash on open. So then a large portion of the design team would be
    halted in their tracks trying to find the one dwg out of thousandsthat was
    corrupt... Once they got everyone onto R2000, this issue virtually
    disappeared, though.
    There were also some issues when trying to archive and get the dwg files
    set up for submission back to the client, but they finally set up some
    routines that would basically copy the files to a folder, detach all the
    xrefs, then purge, audit, etc, and those would be the files that got sent
    out.
    It could get crazy, but somehow, in the end, it all worked out pretty
    well. I have to say that a lot of the success was based on the well
    documented and enforced standards.

    Good luck with your stuff.
    Craig
     
    slacker, Apr 17, 2004
    #2
  3. Thanks for the reply Craig.

    In 18 years of working with AutoCAD, my present position is only the second
    office I have worked in and your description is only the third "mechanical
    system" I have had any information about. My first experience was with a
    small 2 engineer consulting engineering firm and I developed the cad system
    there and it only ever got up to 4 work stations but had been static at two
    for the last 8 years or so. Now it is a whole different ball of wax. The
    biggest project I had worked on was an addition to a secondary school and
    had 5 levels and plotted out to 5 36"x48" sheets at 1:100 scale. I did the
    plumbing design and drafting, another drafted for an engineer who did the
    design and a third did the sprinkler drawings.

    The system you have described looks more compicated then it needs to be but
    then I am starting to get and idea of the difficulties in working with
    multiple users in different offices. I understand the need to lock down a
    cad system and from my experience with starting AutoCAD for even just 2
    stations I can appreciate the difficulties with trying to do the same thing
    with a really large operation. However, the majority of the projects being
    done are not the huge ones spread across many offices and personal but
    simple 3 floor, 150 unit condominium developments or simple renovations to
    existing hospitial facilities generally done by one or two people under the
    direction of a project manager and engineer. Now when you have to split up a
    project the logical split is by system, HVAC, Plumbing, etc. The other
    thing, is that working vertically in one drawing (without using complicated
    xrefs, etc) only needs a level specific layer naming system. With a good
    system, you don't really care what the actual layer name is as long as you
    know what belongs on that layer. Shoot, I am digressing.

    I office system is set up with one dwg file per level with architectural
    backgrounds attached as an xref and layout tabs (number as required for more
    than one plot per floor) for plotting. I set up a separate dwg file with all
    levels of building attached as xrefs and then attached each mechanical level
    dwg file as xref as well. All xrefs are attached as "overlay" as "nested
    xrefs" can get out of had really quickly attached one set of xrefs to the
    mechanical level dwg file and a combined file is no big deal. The only
    information that comes through to the combined dwg. file is the model tab
    mechanical so it works fine. No need for the complication of separate "level
    specific mechanical information dwgs" only. Rename the xrefs, 1-arch,
    1-plumb, etc and with layer 0 current, simply turn off "*" layers, on "1*
    for first floor, and then select "1-plumb" xref for "refedit" and then turn
    on "1-P*" layers for reference. Works just fine. Every time you save the
    refedit changes, you update the mechanical level drawing. You should be able
    to have two or more people working on copies of the combined mechanical
    drawing at the same time, but in different levels without losing any work
    because once you refedit a xref, no one else can check it out for
    editing.(unless you use the load xref with copy which I can't see any use
    for).
    The big problem is that some commands cannot be used while refedit is
    current, such as save the drawing, or copyclip or copy with base point to
    transfer something from one xref to another. You have to redraw the same
    thing that you have shown on one level and need on another level. This is a
    pain and against the basic Cad Principle of only draw something once and
    copy many times. However, once I can get others into the habit of working
    through a building vertically, it is only a small step to go the vertical
    mechanical dwgs with level specific layers. I hope!

    Thanks again Craig.

    Dave Alexander
    Keen Engineering Co. Ltd.
    www.keen.ca
     
    Dave Alexander, Apr 17, 2004
    #3
  4. Thanks for the reply Russell.
    I don't often get many replies form people working in the MEP trades. Xrefs
    are not a problem except for "nested xrefs" which like blocks can get
    confusing very quickly. I understand the principle and keep trying them from
    time to time but always go back to xreffing everything separately which may
    take alittle more time but works just as well.
    I haven't tried "wblock" while in refedit but will give it a go.
    I have always used a separate layer for overlaying xrefs and always make
    sure that the "xref" layer and layer "0" are on when switching groups of
    layers. I only freeze layers that I don't ever want to see. This is a hold
    over from the "old days" of using DOS and 12 mghz "286" computers with 20meg
    hard drives. Using "load with copy" for xrefs just doesn't make any sense to
    me. I always set the "demand load xrefs" to "disabled" and check "Retain
    changes to Xref layers and Allow other users to refedit current drawings
    which by current drawings I take it to mean loaded xrefs. This allows others
    to edit the xrefs and for me to update the same xref in my dwg. ( If you are
    using enabled with copy, does that mean that you don't get the "xref updated
    notification" or if you do, does that mean that the xref has to be copied
    again and if so doesn't that take longer?)
    I find your OL_ABV and OL_BLW concept interesting. I have always thought in
    terms of first floor, second floor, etc. Plumbing fixtures on the second
    floor have drainage piping located on the first floor. My current layer is
    the second floor drainage piping layer, I locate the riser locations through
    the floor on the plan, switch to the first floor layers (everything off
    except my current layer and the first floor layers) and then switch my
    current second floor drainage piping layer to the first floor drainage
    piping layer (leaving the second floor drainage piping layer on) and either
    copy the risers to current layer or simply insert new ones directly on top
    of the second floor ones and then switch again to the first floor layers
    leaving my first floor drainage piping layer current. Damn that sounds
    complicated but not really. As you say, a little scripted buttons and it is
    a click away. With my old system, all mechanical layers began with a level,
    and all architectural floor plans were overlayed and then the xref or the
    architectural dwg renamed to a level architectural plan. Then layers were
    switched relative to the current layer. If I am on one level and I need to
    go down or up I used a "down" button or "up" button which would read the
    level of my current layer and simply turn off all the layers (leaving my
    current layer on) and then turn on all the layers of the next level up or
    down. The same system works for changing "new" layers or entities on "new"
    layers to "existing" layers and "existing" to "demolation" and so on and so
    on.

    I had posted a sample drawing with a tool bar for changing levels on the
    "customer files" . You can find it under the heading of "Multi-Level
    Mechanical Demo Dwg". That is how I would like to work but until I can
    change the layer standard for company which may just be impossible given the
    difficulty of changing the standard for 13 +- offices and approximately 200
    some odd users, that just may not happen.

    Thanks again for the reply Russell, I don't often get the opportunity to
    talk about these things to people who actually do these sort of things and I
    enjoy it.

    Dave Alexander
    Keen Engineering Co. Ltd.
    www.keen.ca
     
    Dave Alexander, Apr 18, 2004
    #4